Originally Posted by LowendinFL But how do you figure the NEC requires the white to be tied to a constant hot when white is the neutral? Speaking of dead shorts... |
When you back feed a switch in residential, you have the choice of two colors, white and black.
If you use black, that leaves a switch controlled white wire. In a trouble shooting process the white wire with the switch off can be confused with an open neutral wire and can get energized by the switch usually while I'm holding onto the stupid thing.
If the white wire is used as a constant hot, it is either on with the circuit or off with the circuit. a much safer situation.
If the white wire is used as a constant hot, any electrician can look at the splice and immediately tell due to having one or more blacks under a wire nut with one white that there is a back fed switch coming out of the box and a black wire that is switch controlled present at the box.
That is why the NEC requires that you use the white wire as a feed only in those circumstances, only in residential.
Electricians get taught: "The neutral is always white but, the white isn't always neutral"
The NEC has also as of 15+ years ago required that the white used in that manner be permanently identified at both ends a different color so the whole color thing should be a non issue but, it rarely ever gets done.