one less variable to worry about. The 220-240 line voltages are more compatible than the lowly 120v available to the US. wonder how much it costs to get that dedicated power line. Not a bar gig equipment item.
How's this true? Globally, you can expect anything from 220 through 240 with tolerances from 200V - 265V, whereas here domestically we typically see 120V which rarely falls below 115V or above 125V under the same conditions. In the US, 120 volts is by far the most universal for end user accessible plug connections.
I regularly pull 14 AWG out and fish 12 AWG THHN in place of it where I can and when I'm remodeling a wall. Otherwise I rewire the wall when I have it open.
But - yeah - just putting a 20 Amp wall receptacle on a 14 AWG run isn't smart - but it will surely beef up the contacts.
Besides - getting rid of the back-stabs for screw connex is the best idea.
Like I said though - it's all for naught if you're on the end of a string of back-stabs with overheated spring retainers and questionable-when-new push-ins that are just folly in a commercial building. People who run 14 AWG and 15 Amp receptacles in a commercial building should have their thumbs broken.
In California (where I have my commercial experience under the CA Electrical Code), back-stab wiring of receptacles is no longer allowed for commercial installations and 15A general receptacle power circuits are strongly discouraged (though not disallowed). Commercial grade receptacles have dual spring loaded wiping contacts (identical for 15A and 20A other than the additional tab). Totally different than typical residential grade. In fact, I don't think back wiring is even available on listed commercial grade recepts. Now because of all the cheaping out of wiring and receptavles in residential installations, AFCI breakers are now required for many areas of a residential building... the cost is probably greater than just using commercial grade wiring and devices!!!
As far as 20A receptacles on a 15A circuit, this is a gray area because you can put 3 or 4 20 amp receptacles on a single 20A circuit which would defeat the purpose of keying a receptacle to the ampacity of the circuit. You can also you more than 1 15 amp receptacle on a 20A circuit. Where things get specific is when you have a SINGLE receptacle on a circuit, a 15A receptacle (single not duplex) can't be used on a 20A circuit and a 20A receptacle (single not duplex) can't be used on a 15A circuit but other than these, in practice the lines are quite blurred and it often depends on the inspector.
I'm not up on the latest code revision as I'm not doing and power system engineering anymore, instead I'm more current on the UL product safety side of things (which is just as confusing).