Quite frankly folks. I’m appalled at the number of responses that want to call in a governmental agency.
The authorities are required as a last-ditch effort to force compliance. This method should absolutely be used against any entity disregarding life safety. Electrical systems are the most likely of any building system to cause a fatality.
I always bring a Furman power strip w surge protection, and the only thing I plug in is my own amp and pedals (and I don't sing): (
Furman SS-6B Surge Block). Does that offer protection in an open ground situation like this venue has?
NO. And whatever protection you thought you were getting for your equipment connected to it probably doesn't work either without the ground.
It means the wiring is old (2-wire), and there's no earth ground for the circuit. If there's a circuit breaker, you should be okay.
ABSOLUTELY NOT! A circuit breaker is unlikely to trip promptly during a ground fault where there is no equipment ground. The equipment ground is multi-purpose. To create an alternate path to ground in case the neutral is broken and for bonding equipment chassis so that there is a low impedance path is back to the source, which in turn causes high enough current to flow through the circuit breaker to cause it to trip quickly. Even that is still not quickly enough to prevent an electrocution. Which is exactly why GFCI's were invented.
NO! A circuit breaker is designed to protect the wiring in the wall from overheating due to more current than the wiring can take. That's about fire safety, not people safety. You can be well on your way to the morgue before that breaker ever trips.
Mr Garage-Bander is correct here. Use of fuses and circuit breakers were intended as equipment protection. Their only life protection was to prevent the building from catching on fire and burning people to death. Which still happens a lot to this day.
The current path is usually not between the mic and the floor, so rubber mat probably won't help in most situations. ...
AFAIK the problem is usually between the chassis of an amp and the chassis of the mixer.
This is correct as to why an electrically insulated mat would not protect you. One night the band after us was playing and the singer was shocked after putting on a guitar which he hadn't played during previous songs. The microphone was electrified, but he wasn't shocked until his fingers were touching the grounded strings of his guitar.
Circuit breakers protect the wire from overheating and starting the building on fire. They do NOT protect you against electrocution - the amount of current that will kill you will not trip a breaker or blow a fuse.
This statement is absolutely true.
Word of caution about outlet testers. Sometimes "grounded" isn't "grounded"
Let me give you a practical example. Bought an old house last year. A couple of circuits are old "BX" metal clad cable with only 2 conductors, no dedicated groundwire. 2 prong outlets. I replaced them with 3 prong outles but there is obviously nothing to hook the ground on the receptacle to. But they have metal outlet boxes and metal cladding all they way back to the breaker box so they read as "grounded" with an outlet testers, even the one that is only metal clad for about 10 feat to a metal junction box and then is "rag wire" back to the breaker box. Hope that makes sense. I know two fingers was an electricians so he might be able to explain a bit better.
This is only partially correct, IMO. As another argued, if the tester shows grounded then it is in fact grounded (or connected to the neutral which is grounded). The metal box through the connector and BX metal jacket is continuous back to the panel which is bonded to the earth ground. However, use of BX jacket as equipment ground is a NEC violation in the USA because the BX jacket is not UL listed for use as an equipment ground. And, since BX cable is no longer manufactured, it will never be tested by UL. In certain cases, metallic conduit is approved for use as an equipment ground so long as is electrically continuous back to the source. I don't believe there is any proof that the BX jacket is not an effective equipment ground path. It's just not an approved method.
On at least one of those runs it is not really grounded, not even close to properly. The metal cladding run about 10 feet to a metal junction box. From the junction box to the breaker box it is cloth covered wire with no ground.
There is a ground, it's the metal jacket itself. It is not "Proper" because the method is not approved. But it's unclear whether the BX jacket is effective.
Yeah, that'll get you rebooked there.

More likely cause the place to get shut down. If the OP reported it to the owners 10 years ago and it didn't get fixed, even with new owners, that means it was too expensive.
In most cases citations are allowed sufficient time to be remedied before fines are levied. This is true with OSHA and most building enforcement. OSHA refers to acts as willful violations when they know that the employer was aware and purposefully chose to disregard life safety.
Don't do that! Seriously... Leave it set to make the proper ground connection unless totally sure that it's only acting in the audio ground, and the electrical ground is hardwired and links to a properly grounded outlet too. 'Ground lift' is a Seriously Bad Idea, it should never have been invented.
There's a document by Rane called "Grounding and Shielding Audio Devices" that goes into this at length, but its an easy read, and has influenced the better habits of modern audio gear makers.
I am not familiar with the Rane document you mention. But if you are referring to the ground lift switch for XLR cable connections that has nothing to do with shock protection. Signal cable drains should only have connection to earth at one end. From mixer to microphone, there is no issue because the mic is not grounded. But mixer to bass amp DI could cause a ground loop due to both devices being connected to ground via the mains.
Because the US is extremely relaxed about Electrical safety
All outlets (and i think actually all circuits) must be protected here in australia , and AFAIK a deathcap amp would never have been approved here, even back in the day.
I wouldn't call electrical safety in the USA as lax, however enforcement is another topic. All NEW residential outlets are required to be either arc-fault or GFCI protected, or both in the latest NEC. Not all jurisdictions in the USA adopt the latest NEC into law. And all existing installations are grandfathered to the version of the code that was applicable the year they were installed. That being considered, you can imagine how difficult it might be to determine violations for electrical systems.
This is why it seems so odd to me to put a whole lot of GFCI's throughout a house on selected outlets instead of a single unit on the mains feed into the house. I guess the benefit is when you have a dodgy toaster it only trips that circuit instead of your whole house though.
Not only would it be inconvenient if your entire house tripped on a GF, but it would also make finding the source nearly impossible. GFCI protection at the outlet is not only convenient but practical in most cases. People are rarely electrocuted on the concealed wiring system. Having the receptacle trip that you are currently plugged into immediately informs you which device is faulty. Arc Fault protection, OTOH, probably makes more sense on the circuit breakers but they are more for preventing fire.
They only have to be up to code when they were built. Any later Including aslteration are also inspected. You would think there would be a little buy-in by the owner for especially if he wants to bring bands in there. They could run an entirely separate circuit if they really wanted to - out of a breakout panel all within code.
Agreed. The cost of remedying the electrical system at the club is nothing compared to a wrongful death lawsuit.
My NEC knowledge is probably out of date considering I took my electrical license using the 2005 NEC. However, I performed arc flash studies and provided electrical safety training for industrial maintenance staff from 2013-2018. I wouldn't call myself an expert. Just someone who knows more than the average lay person regarding electrical safety.