I am a master electrician. Residential grounding and bonding can happen in a number of ways.
The current standard is two ground wires. One to the water pipe and one to a grounding rod.
A ground wire to a grounding rod can come from the main panel. It can also come from the meter base, or an exterior main disconnect. It will usually be #6 copper solid or stranded, usually bare but not necessarily.
A ground wire to the water pipe will usually come from the main panel will run to a clamp on a cold water pipe. Wire size depending on service size. Can be copper or aluminum, bare or coated.
Bonding between ground and neutral should occur at the first point of disconnect. This may be an outside or inside disconnect, or a main panel with a main breaker.
The bonding may be done in various ways. Could be a bonding strap, bonding screw or a wire. Either way, you should have continuity between the neutral bar and ground. Once it is bonded at the first point of disconnect, no other service equipment gets bonded downstream.
Bonding seems to confuse even some electricians, I see a lot done incorrectly.
Don't know if any of this will solve your noise issue. Just wanted to lay out how it should all look.